I have recently installed a pair of CCRs into a data centre in central
London.
The Data centre we are using bills the cost of colo is per U and per VA - £5.00 per U plus £0.70 per VA per month I have as a result discovered
that the power factor of the CCRs is awful!
0.35A 36.1 watts 234V Power factor 42% to 45% i.e. 81.9 VA i.e. £57.33 per month for the power.
I replaced the PSU in the CCR with a Power Factor-corrected power supply
and the results are MUCH better:
0.19A 41 watts 234V Power factor 89% i.e. 44.46 VA i.e. £31.12 per month for the power.
This improvement has made a significant reduction in my colo costs, despite the actual power increasing slightly.
With the new PSUs, my colo cost savings for me are down by £630 approx per year just by improving the power factor of the two CCRs !!! The payback period for the new PSUs was a couple of months.
Has anyone else noticed this? Would be good to get some comment from MT on whether they can improve the power factor.