Thu May 29, 2014 2:26 am
Here is a RB2011 running v6.12.
I was able to monitor several APC Back-UPS XS-1500G units and an older BX1500G unit. I powered all six APC 1500G UPS's up on the same power strip and moved the USB cable from one to the next.
[admin@TEST Router] > sys resou prin
uptime: 41m13s
version: 6.12
build-time: Apr/14/2014 09:27:45
free-memory: 108.8MiB
total-memory: 128.0MiB
cpu: MIPS 74Kc V4.12
cpu-count: 1
cpu-frequency: 600MHz
cpu-load: 4%
free-hdd-space: 110.7MiB
total-hdd-space: 128.0MiB
write-sect-since-reboot: 68
write-sect-total: 6461
bad-blocks: 0%
architecture-name: mipsbe
board-name: RB2011UiAS-2HnD
platform: MikroTik
[admin@TEST Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m
alarm-setting=immediate model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8"
serial="4B1345P23018" manufacture-date="2013-11-07"
nominal-battery-voltage=24V
[admin@TEST Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m
alarm-setting=immediate model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8"
serial="4B1336P39058" manufacture-date="2013-09-06"
nominal-battery-voltage=24V
[admin@TEST Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m
alarm-setting=immediate model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8"
serial="4B1345P23098" manufacture-date="2013-11-07"
nominal-battery-voltage=24V
[admin@TEST Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m
alarm-setting=immediate model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8"
serial="4B1318P38382" manufacture-date="2013-05-04"
nominal-battery-voltage=24V
[admin@TEST Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m
alarm-setting=immediate model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8"
serial="4B1345P23088" manufacture-date="2013-11-07"
nominal-battery-voltage=24V
[admin@TEST Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m
alarm-setting=immediate model="Back-UPS BX1500G FW:866.L5 .D USB FW:L5"
serial="3B1106X26340" manufacture-date="2011-02-04"
nominal-battery-voltage=24V
[admin@TEST Router] >
[admin@TEST Router] /system ups> mon 0
on-line: yes
on-battery: no
rtc-running: no
runtime-left: 17m15s
battery-charge: 100%
battery-voltage: 27.16V
line-voltage: 125V
load: 36%
replace-battery: no
smart-boost: no
smart-trim: no
overload: no
low-battery: no
-- [Q quit|D dump|C-z pause]
This same RB2011 TEST Router will NOT monitor the following other APC UPS's I have laying around:
APC Back-UPS ES-500
APC Back-UPS ES-550
APC Back-UPS ES-600G
Here's the interesting part.
A RB493G with the simple USB power jumper modification can monitor all the aforementioned APC UPS's !!!
[admin@Test2 Router] > sys reso prin
uptime: 12m19s
version: 5.25
free-memory: 244248KiB
total-memory: 257108KiB
cpu: MIPS 24Kc V7.4
cpu-count: 1
cpu-frequency: 680MHz
cpu-load: 2%
free-hdd-space: 79648KiB
total-hdd-space: 126976KiB
write-sect-since-reboot: 5568
write-sect-total: 36885
bad-blocks: 0%
architecture-name: mipsbe
board-name: RB493G
platform: MikroTik
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usb1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS ES 600G FW:905.W1 .D USB FW:W1" serial="4B1311P39220"
manufacture-date="2013-03-15" nominal-battery-voltage=12V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usb1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1318P38382"
manufacture-date="2013-05-04" nominal-battery-voltage=24V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usb1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1345P23088"
manufacture-date="2013-11-07" nominal-battery-voltage=24V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usb1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1345P23098"
manufacture-date="2013-11-07" nominal-battery-voltage=24V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usb1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1336P39058"
manufacture-date="2013-09-06" nominal-battery-voltage=24V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usb1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1345P23018"
manufacture-date="2013-11-07" nominal-battery-voltage=24V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usb1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS BX1500G FW:866.L5 .D USB FW:L5" serial="3B1106X26340"
manufacture-date="2011-02-04" nominal-battery-voltage=24V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usb1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS ES 500 FW:2.e2.D USB FW:e2" serial="AB0312140479"
manufacture-date="2003-03-17" nominal-battery-voltage=12V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usb1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS ES 550 FW:843.K2 .D USB FW:K2" serial="3B1135X25856"
manufacture-date="2011-08-27" nominal-battery-voltage=12V
[admin@Test2 Router] >
Well, maybe the RB493G can monitor ALL nine of these APC UPS's because it's running v5.25? Let's upgrade this RB493G to v6.12 and see if it still can monitor all these different APC UPS's...
How about that! A RB493G with USB power jumper modification running v6.12 is able to monitor ALL of these different APC UPS's!!!!
[admin@Test2 Router] > sys reso prin
uptime: 2m13s
version: 6.12
build-time: Apr/14/2014 09:27:45
free-memory: 227.0MiB
total-memory: 256.0MiB
cpu: MIPS 24Kc V7.4
cpu-count: 1
cpu-frequency: 680MHz
cpu-load: 0%
free-hdd-space: 110.3MiB
total-hdd-space: 127.8MiB
write-sect-since-reboot: 959
write-sect-total: 32276
bad-blocks: 0%
architecture-name: mipsbe
board-name: RB493G
platform: MikroTik
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS ES 550 FW:843.K2 .D USB FW:K2" serial="3B1135X25856"
manufacture-date="2011-08-27" nominal-battery-voltage=12V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS ES 500 FW:2.e2.D USB FW:e2" serial="AB0312140479"
manufacture-date="2003-03-17" nominal-battery-voltage=12V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS ES 600G FW:905.W1 .D USB FW:W1" serial="4B1311P39220"
manufacture-date="2013-03-15" nominal-battery-voltage=12V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1345P23018"
manufacture-date="2013-11-07" nominal-battery-voltage=24V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1336P39058"
manufacture-date="2013-09-06" nominal-battery-voltage=24V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1345P23088"
manufacture-date="2013-11-07" nominal-battery-voltage=24V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1345P23098"
manufacture-date="2013-11-07" nominal-battery-voltage=24V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1318P38382"
manufacture-date="2013-05-04" nominal-battery-voltage=24V
[admin@Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS BX1500G FW:866.L5 .D USB FW:L5" serial="3B1106X26340"
manufacture-date="2011-02-04" nominal-battery-voltage=24V
[admin@Test2 Router] >
That's not all....it gets even more interesting when we start testing CCR1036-12G-4S routers. The first CCR1036-12G-4S is able to monitor ALL nine of the different APC UPS's I have here to test! Yay!
[admin@MikroTik] > sys reso prin
uptime: 2m57s
version: 6.12
build-time: Apr/14/2014 09:27:45
free-memory: 3790.1MiB
total-memory: 3969.0MiB
cpu: tilegx
cpu-count: 36
cpu-frequency: 1200MHz
cpu-load: 0%
free-hdd-space: 905.5MiB
total-hdd-space: 1024.0MiB
architecture-name: tile
board-name: CCR1036-12G-4S
platform: MikroTik
[admin@MikroTik] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS BX1500G FW:866.L5 .D USB FW:L5" serial="3B1106X26340" manufacture-date="2011-02-04"
nominal-battery-voltage=24V
[admin@MikroTik] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1318P38382" manufacture-date="2013-05-04"
nominal-battery-voltage=24V
[admin@MikroTik] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1345P23098" manufacture-date="2013-11-07"
nominal-battery-voltage=24V
[admin@MikroTik] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1345P23088" manufacture-date="2013-11-07"
nominal-battery-voltage=24V
[admin@MikroTik] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1336P39058" manufacture-date="2013-09-06"
nominal-battery-voltage=24V
[admin@MikroTik] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS XS 1500G FW:866.L8 .D USB FW:L8" serial="4B1345P23018" manufacture-date="2013-11-07"
nominal-battery-voltage=24V
[admin@MikroTik] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS ES 500 FW:2.e2.D USB FW:e2" serial="AB0312140479" manufacture-date="2003-03-17"
nominal-battery-voltage=12V
[admin@MikroTik] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS ES 550 FW:843.K2 .D USB FW:K2" serial="3B1135X25856" manufacture-date="2011-08-27"
nominal-battery-voltage=12V
[admin@MikroTik] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS ES 600G FW:905.W1 .D USB FW:W1" serial="4B1311P39220" manufacture-date="2013-03-15"
nominal-battery-voltage=12V
[admin@MikroTik] >
The second CCR1036-12G-4S router I tested could only monitor one of the nine APC UPS's ....Booooo!!!!
[admin@CCR1036 Test2 Router] > sys reso prin
uptime: 6m51s
version: 6.12
build-time: Apr/14/2014 09:27:45
free-memory: 3767.0MiB
total-memory: 3969.0MiB
cpu: tilegx
cpu-count: 36
cpu-frequency: 1200MHz
cpu-load: 0%
free-hdd-space: 902.4MiB
total-hdd-space: 1024.0MiB
architecture-name: tile
board-name: CCR1036-12G-4S
platform: MikroTik
[admin@CCR1036 Test2 Router] > sys ups prin
Flags: X - disabled, I - invalid
0 name="ups1" port=usbhid1 offline-time=5m min-runtime=5m alarm-setting=immediate
model="Back-UPS ES 600G FW:905.W1 .D USB FW:W1" serial="4B1311P39220"
manufacture-date="2013-03-15" nominal-battery-voltage=12V
[admin@CCR1036 Test2 Router] >
[admin@CCR1036 Test2 Router] > sys resou usb prin
# DEVICE VENDOR NAME SPEED
0 2:1 Linux 3.3.5 ohci_hcd Tile-Gx OHCI 12 Mbps
1 2:5 APC Back-UPS ES 600G FW:905.W1 ... 1.5 Mbps
2 1:1 Linux 3.3.5 ehci_hcd Tile-Gx EHCI 480 Mbps
[admin@CCR1036 Test2 Router] >
Here is the USB print from the first CCR1036 that can monitor all nine UPS's:
[admin@MikroTik] > sys reso usb prin
# DEVICE VENDOR NAME SPEED
0 2:1 Linux 3.3.5 ohci_hcd Tile-Gx OHCI 12 Mbps
1 2:2 APC Back-UPS ES 600G F... 1.5 Mbps
2 1:1 Linux 3.3.5 ehci_hcd Tile-Gx EHCI 480 Mbps
[admin@MikroTik] > sys reso usb prin
# DEVICE VENDOR NAME SPEED
0 2:1 Linux 3.3.5 ohci_hcd Tile-Gx OHCI 12 Mbps
1 1:1 Linux 3.3.5 ehci_hcd Tile-Gx EHCI 480 Mbps
2 2:3 American Power Conversion Back-UPS XS 1500G FW:866.L... 12 Mbps
[admin@MikroTik] >
What do the guru's at MikroTik think the issue is?
(1) Why does a RB2011 only see the 1500G UPS's and the RB493G sees all nine UPS's?
(2) Why does one CCR1036 see all nine UPS's, but a second CCR1036 only sees the 600G and no other UPS's?
Thanks for those that took time to read this!
Brad